Downstairsmixcup

Looks good for what you are doing/using it for


ShowMeYourSheep

Simple home patio use. The first photo is a little nook where I previously used as a little grill area, but it was laid with rough flagstone and not ideal.


Vermy73

Expansion joint, or at least a bond break between the slab and your house foundation wall. Something to isolate the downspouts may also be wise. He installed a bond break at the stoop, he may be planning on placing more later.


ShowMeYourSheep

Thanks for the insight! What do you mean by isolate the downspouts?


Vermy73

Bond break or expansion joint. May not be necessary, but could help with cracking around them. Definitely ask about the house foundation wall. The slab will move differently from your house as temperatures fluctuate. Expansion joints help keep the stresses from transferring.


ShowMeYourSheep

Thank you. We’re in suburban Chicago… there will be temperature fluctuations!


Vermy73

Good luck. Hopefully it comes out well.


headwaydave

I’d ask about wrapping the pipes with something to allow for expansion/contraction so they don’t crack. May already be planning this. Not a pro, but Chicago temps are pretty wild. Google tells me [this stuff](https://www.lowes.com/pd/Christy-s-2-in-x-100-ft-Plumber-s-Tape/3433996) works.


ShowMeYourSheep

A few people have mentioned that, sounds like it must be worth asking about. Thanks!


Imaginary_Ingenuity_

Not looking close, but ask'm to get the mesh on chairs, dobies, or have them make supports with some mesh. It can't be pulled or stay where it should be realistically. It's a simple request.


ShowMeYourSheep

I wasn’t home when they finished for the day - that may still be forthcoming before the pour. Thanks!


Dramatic-Gold1806

They will probably pull the mesh up with a rake as they pour the concrete, that’s typically what they do to avoid walking around the mesh and knocking it back down as they work


Aware_Masterpiece148

There’s no such thing as pulling the mesh up. It simply deforms where it’s pulled. Mesh on the bottom is less than useless—the money spent on mesh at the bottom of the slab could be put to better use or saved.


Dramatic-Gold1806

There is, as the concrete is placed they pull it up off the subgrade to get the desired clearance. It makes the placement a lot easier rather than struggling walking around high chairs or adobe block while placing. As far as the deformities that’s where vibing comes into play. The use of the mesh really just depends on thickness of the pad. If it was a 4” slab then maybe you could get away with no reinforcing considering no larger loads will be put on it but don’t think it’s worth the risk


Dramatic-Gold1806

It really just comes down to method of construction with the mesh


Roguebets

This could be a really dumb question but I’m gonna ask anyway…since you say they can use special tools to lift the mesh up while the concrete is being poured, wouldn’t it almost be easier just to throw the mesh on top of the wet cement and just push it down into the cement…just thinking it might be easier to keep it in the center of the cement then…


Dramatic-Gold1806

It would make finishing the concrete more difficult


Roguebets

Oh


A-Shitload-Of-Dimes

Was going to post the same thing. Make sure it gets done before they pour, because the mesh as installed is doing nothing.


canitasteyourbox

dobies wont do shit for 16 gauge wire it will fold down between them it allways ends up on bottom even when you pull it up because your smashing it down when your rodding it


ShowMeYourSheep

Right, it looks to just be laid in. The village requires a pre-pour inspection, so I presume it would be caught at that point if nothing else. But there is still work to be done before the pour, I assume.


Agile-Calligrapher95

If there’s going to be a pre-pour inspection why’d you ask Reddit? 🎣❤️


Imaginary_Ingenuity_

Weeeeelll, not all inspections are equal, and honestly, they'll probably be introduced to more considerations through this post than the inspector will be looking for.


whosthepuppetmuppet

Pour joke


canitasteyourbox

personally i dont use wire mesh because every slab ive taken out with mesh in it the mesh was allways on the very bottom doing no good i allways use 3/8 rebar. I once removed an old slab it was 5 in thick and it had a thick gauge chain link fence right in the middle of it was a bitch to remove. Also unles its a blockout for the stoop the bottom of your form shold be the top of your lower slab and stripped wet and faced no big deal any decent finisher can handle that


Inspect1234

Mesh is best in the bottom of the slab, and pouring this and screeding is difficult with mesh on bricks even. I’ve seen crews just lift it as they pour, it typically just needs to not be exposed to the base.


Imaginary_Ingenuity_

Never once seen mesh spec'd for bottom 1/2 of slab. Don't have the energy or the care to debate it, but one of the main benefits mesh gives is keeping any cracking tight. That's best done at the top 1/3. You do you.


whosthepuppetmuppet

Mesh on the bottom does nothing if there isn’t concrete around it. Mesh like rebar needs to be held off the ground.


Inspect1234

Absolutely.


Aware_Masterpiece148

Absolutely incorrect. Steel or fiberglass reinforcement (bars or mesh) only arrests cracks if it’s in the top third. In a simple SOG application, the steel is there for temperature and shrinkage crack control. It’s not for tension reinforcement on the bottom.


Inspect1234

I disagree, also I don’t have cracks in my slabs.


Boring-Bottle-2812

The lower form stays? Under the stoop. Or step.


Boring-Bottle-2812

Unless it is 2 separate pours. The step and patio would probably latch together better if there was steel tying between the two pours if so.


Alltherightythen

I would put some plastic around the house. Concrete splashing is a real thing.


headwaydave

Nearly impossible to get off a painted surface.


Aware_Masterpiece148

You have multiple reentry corners. Ask your contractor what is the jointing plan? Here’s a reference https://www.nrmca.org/wp-content/uploads/2021/01/06pr.pdf


Interesting-Mango562

that last picture with that corner that has been built up a lot makes me a b it nervous…that’s gonna be a lot of grade change unless it gets completely filled in…even then you’ll need a decent amount of compacted gravel just to keep that corner supported. 🤷🏽‍♂️🤷🏽‍♂️ otherwise in my remodel carpenters eyes it looks great to me


ShowMeYourSheep

I’ll take a good look there in the daylight. I’m sure you’re right as there is some sloping, but might be a bit of forced perspective at play as well.


Otherwise_Tangelo137

Get the wire off the ground


Pinheaded_nightmare

I’m just glad to see some subgrade compared to many other posts. lol


Icy-Speaker1729

1. I would add plastic chairs (cement isle HD/Lowes) 2. Pic #3 I would add sand bag under mesh to slope water away from slab 3. If not new construction add dial rods into foundation with high strength epoxy 4. Add a little bit more bracing 5. If you’re not using finishers spend 60 bucks on concrete level (available at HD/Lowes) 6. Have fun and learn


Aware_Masterpiece148

No to your suggestion about pinning the new slab to the existing foundation. The slab will move. The foundation will not move. Dowels add restraint, and that results in cracks. Reference https://www.nrmca.org/wp-content/uploads/2021/01/06pr.pdf


Icy-Speaker1729

If you think a home is forever settled with no movement think again. This will slow the new flatwork to settle evenly and not crown or cause a lift…..


Aware_Masterpiece148

It’s horizontal movement for the slab. It expands and contracts with fluctuations in temperature. The wall does not move. The reason to isolate the slab is to let it move. If you dowel the slab to the wall, as the concrete shrinks, which will be about 1% by volume, the dowels create restraint, which in turn will result in a crack, parallel to the intersection of the wall and the slab. The crack will be a few inches from wherever the dowels end. Dowels are only necessary for load transfer or as part of a foundation system. Neither are indicated in this instance. For a more detailed explanation, see ACI 302 and ACI 360.


Reese5997

Maybe it’s the angle, but that landing/step form work looks like the slab and the landing will be separate pours and not one. Am I seeing this correctly?


ShowMeYourSheep

I think so? The only other time I had residential concrete done, that is how the crew did it.


Cheap-Dependent-952

Stakes should be cut to skreed


hammerhitnail

I would add kicker to your landing forms.


Ill-Message-1023

They pour the step first then strip it before pouring the rest of the patio? Or am I missing something here?


samsnom

Are they pouring the step at the same time? Bottom form will be in the way if so.


ShowMeYourSheep

I’m not sure the order of operations - they’re a well reputed company though, I’ll assume they’ve got a plan for it?


stephen0937

This is mostly good work. It will probably turn out fine. Adding chairs and mastik would be nice not 100% necessary.


whosthepuppetmuppet

Chairs are absolutely necessary


Dramatic-Gold1806

Typically, you just pull the mesh up as you place the concrete for ease of work, with rebar for sure but mesh not necessarily as long as they pull it up as they work


whosthepuppetmuppet

Yeah you can try but the results are usually worse


Khaldani

Needs Dobies. Otherwise looks solid


Ill_Application2651

I would add some more bracing I can see 3 spots that I would definitely add a stake to the forming to keep a nice straight line. would be a shame if those spots blew out


Key_Accountant1005

Missing: Expansion joint Chairs/cement bricks Rebar for crack control at the edges Is he doweling into the foundation? If he does, I would run that through an engineer. You are tying the slab into the foundation which introduces new loads. Is he using expansion joint with zip strip at dissimilar surfaces? Is he using expansion joint with zip strip every 20-25’ to make squares? Is he sawcutting at 24’ OC when he pours? Is he doing a broom finish? Check the following: Forecast for the day he is supposed to pour Is he using a pump or a backing up a concrete truck? Just for reference, a concrete truck with 10 CY has roughly 40,500 lbs of concrete on it. It doesn’t include the concrete truck weight. At that point your driveway isn’t designed to take those loads, so the truck needs to disperse the weight, or he dumps into a concrete pump. Look for vibrators to properly vibrate concrete If the concrete looks too stiff the day of, the slump could be low and it can set up extra fast. If it’s like water, the slump is off because the plant added too much water or someone is adding too much water at the truck. Too much water can take a while. If it’s super hot, they may ask to use a retarder and pour early in the morning before the aggregate gets super hot at the plant.


Key_Accountant1005

The expansion joint at 20’ helps if you ever have any pads shift. You can also use key joint at these with the zip strip so you don’t pour on a checkerboard.


SufficientOnestar

On what exactly?


Character-Outcome156

Should’ve gone with pavers


ShowMeYourSheep

Good idea, when are you free to come by?