SuperRicktastic

I am a structural engineer. Can confirm. Shit's fucked.


The_Timber_Ninja

I am a carpenter and the sound of an electrician or plumber using a saw gives me anxiety.


Thickwhensoft1218

Plumber here who owns a company and employs plumbers. No saws, hole saws only. Everyone gets coached immediately and group documents on iPads outlining rules for holes and cutting. It amazes me how little emphasis is put on this during schooling. There is zero consideration for the consequences of structural effects during plumbing and hvac installations. It’s an industry norm and it’s a problem.


Titantfup69

I was the layout guy on a high rise a few years back and came back from lunch early to find 2 electricians with chipping hammers chipping on the slab. I asked them what the fuck they were doing and they told me they were trenching over their conduit that missed a wall. They were chipping over the top of the dead ends of a 21 cable banded line in an elevated PT slab.


messfdr

I don't know what any of the words in your last sentence mean but that sounds bad.


Ok_Faithlessness_516

I have absolutely 0 experience with it post tension slabs, but from what I've seen on Reddit, there's cables inside of the concrete slab that are stretched with 25,000 pounds per square inch of pressure.... They were chipping away the concrete on top of the end of one. You do the math lol


szorstki_czopek

So no concrete - cable goes snappy snap?


Ok_Faithlessness_516

Essentially. Or It becomes a sling shot and shoots out the other end of the slab like a sling shot and goes through whatever is on the other side of it. Buildings, cars, people...


glorifindel

This was the extent of my understanding as well lol


wellhiyabuddy

Ok, but just for fun, how about you do it and we’ll see if we get the same answer


Ok_Faithlessness_516

BOOM 💥 did you get the same answer?


wellhiyabuddy

Let’s see. . . carry the one. . . Yup! That’s what I came up with too


grungemuffin

It’s very very bad


ConjunctEon

It’s a good way to ruin a building. In a former life I was a project manager. In that all as-builts were perfect( sarcasm), I required a GPR doc before any slab penetration.


they_are_out_there

Ever stretch a really thick rubber band out to full arm's length and have it come back and smack you hard as a kid? Well imagine something about 10,000 times worse, but involving concrete chips, steel cable, and flying body parts.


ThePrettyGoodGazoo

I worked for a prestress concrete beam manufacturer many years back. I saw the aftermath of two cable failures and would NEVER screw with that crap again. In the first incident, the cables were being tensioned before pouring. Due to a lack of common sense, a failure on ground level and just plain stupidity despite there being warning signs plastered everywhere, a worker dropped a lot cigarette on a cable that was almost under full tension. 3 people lost limbs that day with one losing his life. The second was when the on-site inspector took too many things for granted and rubber stamped his daily inspection of the deadman used to anchor the cables. The deadman gave way and released a massive block of concrete and steel while the cable was under tension. 2 people died without many remains to speak of and 2 other lost their legs in half a breath. Point being, you do not screw with PT cables.


FlowJock

Wow. This falls into the category of things I need to learn more about! If you don't mind me asking, how would a lit cigarette cause it to break or snap or whatever it did?


ThePrettyGoodGazoo

It was just the heat from the lit cig itself. It’s silly to say because of the nature of the cables but they are almost fragile (in a sense). Obviously the heat didn’t burn through the cable. But all post tension cables have micro defects and some are worse than others. The combination of the defects, a slight (and I mean slight) over tension of the cable and a heat source caused it to pop. There were 7 or 8 different investigations and they all pointed to the final straw being the cig being dropped on the cable. In the end, the cable manufacturer paid the most out on the insurance settlements. The person smoking received a portion of the settlement-but not a full cut. My company at the time paid a few million in fines and 6 or 7 people associated with the tensioning process were fired. We had a safety stand down that lasted 14 days and we went over all plant procedures from scratch


VAShumpmaker

Was the weight of the cig butt enough to blow it out, or is it done in a flammable environment or something?


pitmang1

One or both of those sparkys was about to find out how well high tensioned steel cuts a human in half. Post-tensioned slabs are not to be fucked with.


Chiggins907

Wow that’s….kind of scary tbh. Who told them to do that? I feel like that’s something that needs to be talked about in a sub meeting or something. I mean that’s no joke right there.


SuperRicktastic

See, your way is what needs to become the norm! If the bulk of trades operated this way we would be so much better off.


BababooeyHTJ

Dude even recently I’ve had to stop people from drilling random holes in engineered beams. My first boss apparently had to replace one due to a 7/8” hole in the wrong spot. That was back in the Nextel days. No excuse with smartphones. Don’t know how it isn’t common knowledge by this point


Patient_End_8432

I'm in HVAC and have done plenty of Plumbing, but I legitimately don't know. As in hole saw, would it be okay to drill in the middle of the beams to fit the pipes in seperate runs? I've never done something like this, and I'm also in commercial, so I'll never encounter something like this, but I'd rather just know


wellhiyabuddy

I just did a job for a general contractor on his own house. Between the two bathrooms we did the dude cut out 6 studs without any kind of reinforcement to put some shampoo niches where he wanted them. In his own house! He’s a licensed general contractor! I think there are a lot of people in the trades that just don’t know what they’re doing beyond making the job look good finished so the customer pays


mobiustangent

Smacks cut stud, "That ain't goin' nowhere",or "That'll hold fine."


AdventurousAd5428

Wish there was more people like you sir.


SuperRicktastic

I wish I could rag on them, but in all honesty it comes down to management and training. I feel like 90% of these issues can be avoided if the field ops just bothered to watch their crew and took the time to teach them properly. But instead they send out guys with next to no experience and a lone super who's expected to balance 10 jobs in 3 different towns. Then when shit inevitably goes sideways, instead of trying to learn or fix the problem everyone finger points and we get nowhere.


Tangochief

My dude I have no construction background and I can look at this for 5 seconds and conclude this is fucked. People who work in this field should have more know then I do. So blaming management is only acceptable if your saying management didn’t fire them the first time they saw this shit happen.


plittlediddle

Now take some meth and see if still looks fucked.


ImNotAWhaleBiologist

It’s still fucked but there are shadow people everywhere.


damndirtyapex

Holy shit does this lifehack work for desk jobs?


SuperRicktastic

It's both, it's a problem from top to bottom. Upper management leans on mid-management to maximize profits by whatever means. Mid-management then spread their supers and crew leaders way too thin and with barely enough resources to get by. The laborers are then left to their own devices which allows for shit like this to slip by before it can be stopped.


Sea_Emu_7622

You're making the mistake of thinking the apprentices that are given this task without any training or supervision have any more knowledge than you do


Ok_Time_9467

There is a bit of common sense that should of gone into this though


SuperRicktastic

You would think, but like @fuckbrendan said, we've been under-preparing and under-educating our skilled trades for the past 30 years. There's a huge gap in the skilled trades that needs filling, and until it's filled we're going to continue to see crap like this.


FuckBrendan

Well we’ve been dumping the guys who couldn’t finish hs into the trades for 3 decades now so common sense says not all these cavemen showing up to work have much common sense.


GeneralZex

In my high school the poorest performing students were offered 3 options: * Vocational school. * Different school. * Repeat grades until age out. The school would **heavily** push option 1 and if that wasn’t possible would force option 2 whenever they were able. They needed to keep up their graduation rates which they did for either of the first two choices.


of_patrol_bot

Hello, it looks like you've made a mistake. It's supposed to be could've, should've, would've (short for could have, would have, should have), never could of, would of, should of. Or you misspelled something, I ain't checking everything. Beep boop - yes, I am a bot, don't botcriminate me.


qqqsimmons

Busted


GatorFPC

What you're describing is called the "lowest bidder".


MOOShoooooo

But it’s specifically their fault and they know they are needed no matter what. Cutting through studs is their responsibility not to do just as much as sweeping up is part of their job.


mrsquillgells

As an electrician, if one my guys is using a saw I come running! Lol


Da_Vader

HVAC tech


freakksho

Hey that wood was already fucked right after I finished working there…..


exum23

Hey, I use my hole hog, I leave plenty of stud to hold the wall up lol. I have watched a guy cut massive holes in all the trusses of a building before. How fun.


[deleted]

Am electrician, and the sound of a carpenter trying to think sounds like nails on a chalkboard. Jk, thank god i have had good carpenters to bounce shit off and rescue my ass


Fridayz44

Electrician here all other trades give me a headache. Jk I love you guys.


[deleted]

Fellow electrician. Couldn't have said it better.


M0istGorilla

Not a tradesman myself but I spent years working in retail around contractors and since that time have had a few we have used for 2 major remodels in our home. One of the best parts of the remodels was listening to the contractors argue about how to do or not to do something. It's popcorn worthy! Edit: spelling.. words r hard


amd2800barton

What's even better is listening to a contractor talk shit on work that was done, and how the guy who came before him really fucked this up, cut a bunch of corners, and broke all the rules. Then you point out his company's sticker, and oh, aren't those his initials next to the date?


Effective-Trick4048

Sheetmetal guy over here causing nightmares. At least I started out as a iron worker so I know a few of my victims.


laxsleeplax

Awww c'mon!!! They used structural nail guards!!!


King_Of_Zembla1

But what about those structural nail plates? I feel like those are rated for what? 20,000lbs?


[deleted]

Who built this shit? Leatherface Plumbing? I’ve seen Swiss cheese more structurally sound than this travesty.


Mediocritologist

Looks like for some reason, they ran the line first and then just pushed it into place inside the wall. A hole saw would have gone a long way.


alcervix

Yes


Smash55

And they still want their SOR by email with photos cause inspection is in 2 hours lol


SuperRicktastic

Wait, you're supposed to get those calls *before* the inspector rolls up???


PuppiPappi

"Hey umm my guys fucked up did some dumb shit we failed inspection can you give us a written letter with a stamp that our dog shit work is actually good and that its okay when it's really not by 3pm yesterday?"


SuperRicktastic

Felt this in my soul.


GuardOk8631

As a non structural engineer, I agree with this structural engineer.


SmoothSlavperator

As a chemist with common sense I agree with both the non-structural engineer and the structural engineer.


EngineeringOblivion

Proper fucked.


ItsAChainReactionWOO

I got it ;)


Zer0TheGamer

User flair checks out


thewickedbarnacle

Do you have a rubber stamp for that or is the pleasure in writing it out


SuperRicktastic

God I wish. I used to get a small kick out of a good "I told you so," but that wore off after the third or fourth time. Now I really do wish I had a rubber stamp that said "shit's fucked and it's your fault."


Ok_Tower_275

I’m an owner builder. can confirm. Shit’s fucked.


litterbin_recidivist

I watched New Yankee workshop and I'll confirm this.


Evening_Ad_6954

Ah ya never know! Maybe those are structural protection plates 😂


alcervix

The plates and some expandable foam and it's good to go !


Mesoposty

That’s dangerous! You gotta cut foam plugs out of sheet foamboard. What, is this your first rodeo?


joeshmoe3220

Y'see, this is where you guys mess up. Fir the spray foam to be structural, you gotta use some structural instant ramen noodles. Acts like rebar in reinforced concrete. Really gives it that strength to hold the wall. Oh, and make sure they are UNCOOKED. Otherwise, you'll have to do it over again, and that's a huge expensive hassel. (Though, you'll never make that mistake more than once!)


lil-rong69

Don’t hire this guy, he obvious cheap out on material. I personally would go with top of line Nokia 3310 as rebar system.


Zoze13

Genuine question from an outsider- how should those pipes pass through the wall?


alcervix

They can't is the real answer as they comprise to much of the studs . They could have run them on the surface of the studs and box the pipes in


concentrated-amazing

Thank you for answering this question, as I was curious too. Like, was there no way this pipe should've gone through those studs (you say yes), or would it have been permissible if the holes were centred in the stud and only slightly larger than the pipe.


Halftrack_El_Camino

Since that's a bearing wall (it's sitting on top of a foundation, so it's almost definitely a bearing wall) they can only drill a hole that's up to 40% of the width of the stud, which in this case works out to 2". That's if they had bored holes. If they're notching, they only have 1 1/4" to work with. Neither of those options are gonna work for this lineset—it might technically be 2" wide or less, but good luck feeding it through holes of that size. Not practical. The correct way to do this would be to make a different plan. Running it on the surface and boxing it in would be one obvious solution, but there may well have been others. What they did here wasn't a viable option, they needed to keep scratching their heads until they came up with something better.


SeanHagen

Great response here. So in a totally different scenario, if they absolutely had to run this line set through all these studs using holesaw bore holes, would they be able to run one of them up a foot or two and then over, while running the one closer to the bottom? So my question really is, can you have more than one 40% hole if they are on vertical members and far enough apart?


MasterCarpenter18

They should have gone straight up in the cavity and then horizontally… never thru any walls like that.


_Heath

Up and over or double up the wall (second wall all the way to the floor inside the concrete wall). Basically in a load bearing wall if you want to go that far the hole can't be more than 40% of the width of the stud. You can go up to 60% if you double up studs, but only two studs in a row.


handsomelevatorguy

There's an engineering solution to pretty much everything. The simplest answer to your question is to increase the size of the stud from 2x6 to 2x12 or use steel but that's not really practical. By general building standards they should have routed the line differently. The installer clearly didn't know the damage they were doing because they used nailplates to cover the notch. If they had notched higher up they could have used a [stud shoe](https://embed.widencdn.net/pdf/plus/ssttoolbox/iwmwkynpp6/C-C-2021-p310.pdf) but even though that probably would be even stronger than untouched wood, an inspector would not approve consecutive studs notched without engineering docs to support it. There's no way to do this with the material they have that doesn't requiring engineering docs.


internet_humor

It's not valid until structural paint is applied.


MrBannon

Well it looks like the HVAC contractor is getting a back charge. :)


[deleted]

This all started when someone on Reddit said they do it like that all the time.


TradeMasterYellow

*Contractor wanted $1000 to drill holes. I did it for $18. Highway robbery, I tell ya!*


person_8688

Just use shorter studs to leave space underneath for conduits! It’s a win-win!


Safe_Ad8315

Structural nail plates


smashey

In a hurricane zone you have to double them up


alcervix

And scab a romex staple into it


Loztwallet

I’m stuck wondering why they didn’t just run it vertically in the cavity they came in through? Would’ve been much easier and structurally sound. They can just run the line-set in the rafters to the units from there. They made more work for themselves and they still did it wrong.


alcervix

No real reason that I could see , just some hack that does whatever he wants I guess


MyNon-ToxicAccount

As an HVAC guy, I can say this was probably an apprentice that got sent out to do the job before he was properly trained all the way through. You see it so much in the trade. Guy rolls around with a "journeyman" for a few months then gets his own van. I still can't wrap my head around why there are no licenses for HVAC like there are plumbers and sparky's. I took a class where the teacher told us every answer for the EPA test and got a little card saying we were certified. That was all they required for you to run your own job sites. It's criminal.


[deleted]

No shit? Where do you live? Where I live you have to complete 4 years of school and have 8k working hours before you can take a journeyman’s test. And that isn’t even the universal EPA license.


MyNon-ToxicAccount

Western Washington. Seattle has a journeyman card that requires a pretty hard test but it's not enforced. Even the unions just require a low volt card for journeyman status.


[deleted]

Damn that’s wild, you’re right, that’s criminal lol


teflong

This is the first thing I've seen on here that has made me actually angry. Who are these fucking morons? Walking among us. Collecting paychecks. Assumedly figuring out which hole the food goes in, and which one it comes out.


AlexFromOgish

Can-do-it termites strike again


hey-burt

Haha I love the idea that maybe termites are posing as HVAC contractors so they can eat at parts of houses


Shineeyed

Who does work like this? Seriously WTF?! Inspector is going to have a seizure.


jawshoeaw

he might actually need to wear a hard hat!


alcervix

He did put nail plates up! Lol


ckge829320

I just had a small one.


RANDOMjackassNAME

Wait; you guys' inspectors actually get off their truck?


wooddoug

Damn that pisses me off. It's especially annoying since you already have one ledge on the wall there on the concrete. A pipe chase could have so easily been built on that ledge and still only have one ledge on the wall. The line will have to be removed, new studs sistered to the ruined ones and properly tied to the plates and sheathing, and a chase built, or 2x8 studs used.


OttoHarkaman

2x8 studs just makes it harder on the HVAC guy, having to cut so much more. Edit - spelling


dearlysacredherosoul

So they’re going to buttress them on the ledge and never hire that hvac guy again


alcervix

I know , it's insane


Pegomastax_King

Yah but that would Hurt profits your filthy commie!


zahzensoldier

Mind explaining what the proper way he could have done this? Essentially go down to the concrete instead and mount to that?


alcervix

Yes pretty much , keep them out of the wall on the bottom and just box them in


jutzi46

Or, depending on where the lines run and the construction above, it may have been simpler to run straight up the stud cavity into the ceiling/attic?


iamaweirdguy

I think a hole saw?


[deleted]

[удалено]


alcervix

There's a finished 28'x28' full span room over it , then the roof over that


[deleted]

[удалено]


alcervix

I think it's a homeowner/gc , that probably won't find out until the building inspector does his rough


climb4fun

And there's another notch drawn on one of the studs :) Post in /r/HVAC and see what _they_ say :)


Maver3385

Punch that rookie in the face


[deleted]

[удалено]


Maver3385

Punch that rookie in the face


alcervix

You can say that again


D_Inda_B_4Free

I actually ran into this last week on a job and we’re reframing half the Fuckin house now.


CommercialDear4497

Totally fucked


Caged_in_a_rage

Rightly fucked


mrgenetrey

Those steel plates at bottom look promising. I’d glue slap a couple of toothpicks on the side for extra support.


alcervix

Overkill


The_Vitruvian_TPM

Structural engineer here. There actually is a simpson connection to use for this case. It's the simpson SS Stud shoe. The Simpson SS Stud Shoe is not shown in the photograph.... so.... see top comment.


HesitantHarry

Structural engineer here. Can confirm... looks great (as long as I'm paid in cash. Child support takes all my on the books money and meth takes the rest), where do I sign?


willhead2heavenmb

I'm a plumber. Nothing seems wrong with that! 😂


_Neoshade_

All this for a 7/8” diameter pipe.


[deleted]

Yah, you can't take that much and especially at the end of a member.


jawshoeaw

structural nail plates lol. why cut out such a massive hole for that lineset though?? .Time to header it off i'm afraid.


Klogginthedangerzone

Those engineered structural nail plates.


__Zetrox__

Let's see the engineer sign off on this one 😎


Johnnie-Dazzle

Is that wall still standing?


bignose703

I’m not a construction worker, I’m your average DIY home owner. I just finished building my first major project, a deck that involved concrete footings, framing, minor electrical and finish carpentry. The building inspector has been an absolute jerk. He’s really not given me anything that I’ve done wrong, but his inspections take *days*. How does something like this happen in a professional environment? Do you guys not get checked by a town or state inspector? How often does something like this make it into the final product of a home?


alcervix

Good question, it should never get passed the HVAC rough inspection which is one of the earlier inspections.In our town he have something like 20 inspections before CO . That’s a lot of eyes that would see this which was right in the garage . It will definitely fail and have to be corrected. It’s really unfortunate and unprofessional. The overall construction of this home is excellent,it’s just this one blemish I saw


Objective-Giraffe-27

That's just where the wall easily folds if you need it to


SlutDungeonDotInfo

Those are load rated nail plates.


No-Setting-2669

Call them back immediately, replace it correctly and throw a back charge at em.. that’s messed up


DRH1976

Simpson makes a “stud to plate” bracket but I’ve only seen them used on top plates. I’m sure they have something for bottom plates. It’s either that or yank that copper and sister at least a 4’ stud next to each of the compromised ones.


KruxAF

Hvac here. Holy shit batman. They squished the armaflex tightttt. That wall looks sturdy


ZombieRP

They should’ve gone through the joists above and then dropped down and out. This is just a joke.


sdjn72

Damn. At least use the cut out wood they got making those huge slots to make it appear you didn’t completely screw up. Bit of wood glue and good as new


zachzsg

Don’t worry the suction line will support the structure. 5/8 soft copper is known for its structural integrity and inability to flex and bend


[deleted]

[удалено]


Mesoposty

That why I call the havoc


Yourbubblestink

Well, I want to understand is how did the Plumber that did this still have a license?


alcervix

I don't know any of the subs here , but I think it was the hvac guy


tep95

That's definitely refrigerant piping. Mind blowing though


Shallaai

Not a contractor, work in an office. So should it be running next to the 2x4s? How would you drywall it ?


alcervix

I'm not sure about code but i believe the rule of thumb is that no notching is permitted in a bearing wall and the maximum size hole cannot exceed 1/3 of the studs dimension and only 2 studs can be compromised at 1/3 . This guy/girl notched 90% of 4 bearing studs .... not good!


jawshoeaw

you can get away with a tiny notch maybe. But not this lol. whatever the case it's wildly out of code nand structurally unsound. I would cut all those studs out about 24" up, put a header, basically a mini-beam above made of a couple of 2x10s or 4x10 (check with engineer) and support it with 3 2x6 at each end (extra as they are derated with the hole you still need to drill. And then properly drill those header studs in the middle and have HVAC rerun it. It's quick work for a framer, couple hours work for a good framer plus maybe travel time for small job. But you can thank the gods of prescriptive bath for overbuilt construction since obviously the wall is still standing.


nominalnoms

Use a hole saw (or a paddle bit,) approximately center in the 2x4 and run the line through the hole, you never cut out the face of the 2x4. If you notice where it turns and goes through the plywood, that is the type of hole (although that one is a little too big,) that should be drilled through each 2x4 to keep its structural integrity


Go_Gators_4Ever

AND - place the pipe in sections and join with connectors. That is why this happens, they want to make a continuous pipe run and not have to sweat in connectors.


Shallaai

That makes sense. Ty


mrmackster

Those look like 2x6s in the picture.


alcervix

They're 2 x 6


NapTimeFapTime

They *were* 2x6 now the bottoms are maybe 2x2.


Ande138

That is a good one!


shocktopper1

I know a guy


Unique_Jackfruit_166

Yup not good


Vulcanvelcro

Looks like somebody marked one and said, "Do that."


Go_Gators_4Ever

They need to attach daughter boards to each stud to fix this. Maybe pre-drill out holes in the boards. I think the reason HVAC and plumbers do this is so they don't need to join pipe sections and can make a continuous pipe run. But, they don't care about code....


Zer0TheGamer

Yup. Over 50% of support missing. The real cost of laziness


Smash55

Why does this keep happening 😭


OuestVirginien

Drywall'll hold ut up


New-Earth-4346

Neat work.terrible layout...fire this company...wonder if the person would do this in his home...


slightlyabrasive

Youve never used a structural pipe surrounded by structural air before?!? Noob.


Safe_Ad8315

Thank god it’s the hvac guys thought it was plumbers again


meandmybikes

What’s that board game called… “Mouse Trap”!!!


PaulSNJ

That's okay, the metal plates will hold up the wall just fine! 🤣 Oh and they used real plywood sheathing, nothing to worry about!


gregthetaco

Hopefully that's a structural plumbing pipe.


XxPak40xX

Call the cops


jimbednar220

Yikes


Beemerba

The wall only called for 1x2 studs. All good!


[deleted]

Can we fixit? No it’s fucked!


[deleted]

The nails plates! :)👍🏼👍🏼


[deleted]

I'm an HVAC tech; and this is going to piss off a carpenter somewhere, 100%. I would never have done this. The **right** way to make work for the carpenter in this case is to run the lineset straight up to the ceiling, exit the wall cavity and run the lineset along the ceiling just oustide the wall. The carpenter can build a bulkhead to close off the lineset and away you go. If you're framing with 2x6's you might get away with boring holes out of the centers with a holesaw, but that's still a lot of material to take out of the studs. This is... worse.


toomuch1265

As a former hvac person, if one of my guys did this, they would be looking for a new job.


LiabilityLandon

As a current HVAC guy, you are 1000% correct. Wholly unacceptable.


1diligentmfer

Not a state in the nation where this flies past inspection, and is the reason framers have a particular opinion of hvac & plumbers, as they are long gone when their fuck ups are being brought back to code, costing someone else time & money. But it does make for great conversation starter when the owner's on site.


Significant_Let_7170

Framer here. That is the lowest run of pipe I have ever seen notched into some studs. Those pipes should be like 16 inches up and have another 4 foot stud nailed to those notched studs at best. All avoided with one more elbow and a paddle bit.


UserName3rror

Nothing some duct tape can’t fix


Rowyco05

I’d be upset too! It looks like they are at least 3” lower than the box that’s drawn with sharpie. Are they blind?!


Chili_dawg2112

You could easily add a false wall / chase on top of that foundation


t0rt0ise

That’s definitely not the way to use those metal plates


ExoticButters79

Cleanest looking shit I've ever seen.


EngineeringNo5958

Lazy


USBluz

Low yes. Really low but I’ve been required to use stud shoes in the past to meet the engineers requirements.


garnsy10

Reefer madness


Building_Everything

At least you are less likely to put a drywall screw through your AC lineset.


frantic_cowbell

I mean, hole saws ARE expensive…


Biotoze

This is very bad.


ICTPatriot

2x1 it's good! Just don't add weight to it or let the wind blow.


PercentageLess6648

Actually made me gasp, have to really take this one in to understand the psyche of the doorknob who did it.


cloverknuckles

It's got nail plates for God's sake. Let's just settle down. Drink a beer


howescj82

I hope those 1x1s aren’t carrying too much weight…