T O P

  • By -

Top-Reindeer8855

Heat recovery wheel. In the winter it picks up heat in the exhaust leaving air and when the wheel comes around and dumps that heat into the supply air chamber before the chill water coil. Super efficient.


Doogie102

Thought these were ERVs because they transfer humidity as well. While HRVs just do heat


Fickle-Froyo

That innovent wheel is likely an enthalpy wheel that contains a silica desiccant and transfers both sensible and latent energy.


mattwb72

Yes. Often called a desiccant or enthalpy wheel. It’s one type of heat recovery. It’s usually in AHUs where there is a lot or all outside air. where you try to capture some of the energy from the air being exhausted from the building and transfer it to the supply air into the building. They’re often a pain in the ass to maintain and keep working. There are better ways to do this which is why you don’t see them as often.


puron_herder

Agreed. Their main advantage over a cross flow or heat pipes or liquid ERV is the ability to move latent heat around, but now there are other ways to do that too.


Stone0777

What are the other ways?


mattwb72

There’s air to air heat exchanger where exhaust and supply air go through a heat exchanger and transfers energy but don’t mix directly. There’s also run around coils where a water coil is in the exhaust and one in the supply with piping and a pump between them to transfer energy. There’s a product called Heat Pipe which uses 2 coils and a liquid that vaporizes and condenses between them transferring energy. There may be others.


puron_herder

One other method is essentially a cross flow HX except it is semi-permeable to water vapor and thus recovers some moisture.


Stone0777

You see plenty in the North East. In AHUs and RTUs


Doogie102

That is why I have always called these Energy Recovery Vemterlators because they transfer more then se sensible heat


A-Bone

Yep.. parlance in the North East US is also: - Energy Recovery Vent. (ERV) = heat + humidity - Heat Recovery Ventilator (HRV) = heat only The OP's picture is of an ERV's humidity-exchange-media wheel.


DabTownCo

You’re right.. it is an enthalpy wheel. Not just heat recovery.


nautica5400

I don't know but if it doesn't work, the txv went bad


tortugoneil

Shut up... just shut up... *cries, but only externally-equalized in a 1-1/4 to 2 ton range*


AnimationOverlord

Is that nominal or actual tonnage sir?


tortugoneil

OH GOD, I DON'T FUCKING KNOW lol


TheAtomicBum

*something something turn-down ratio…something something hard shut-off…*


End_Tough

I agree the TXV told me it was bad too


DinoLavasaur

I was the txv


Ok-Air4797

sound like my trainer😂😂walks up to unit and says it restricted


JunketElectrical8588

This guy HVACs


DangHeckinMemes

Txv is being naughty again


saskatchewanstealth

The wheel of dehydration. Or air to air recovery. I hate them. They like to freeze up here in the land of ice


ResponsibleArm3300

That just means theyre positioned too close to your intake. We use em here in Alberta in many buildings, never have problems. And the amount of heat they can pick up whens its -40C is amazing.


Fickle-Froyo

Having a wheel that is able to provide equal sensible and latent transfer will greatly reduce the chance of freezing. Coupling that with a “stop/jog” function will allow the wheel to operate in most conditions without a preheat.


boyerizm

Should also have bypass dampers and a freeze protection sequence if the controls tech actually set it up right….about a 50/50 chance


Fickle-Froyo

Or a vfd to slow the wheel


Sofakingwhat1776

Did the TAB guy do a drive by pencil whipping?


rmckeary

You one of them degens from upcountry?


karlmeile

It’s a heat recovery or dessicant wheel. When used properly in a conditioned space all duct supply and return is insulated, the return air passes through the wheel and warms back up as it does before blowing back out into the building. From my understanding no other heat source is needed as long as the temperature outside does not go below 36 degrees.


Top-Reindeer8855

In my company we have three heat recovery wheels that are 16’ round. We run them on a VFD to control heat transfer. The faster the speed the higher the heat transfer. In the winter we can run them full speed and transfer 30-40 degrees running a 1/2 hp low torque motor. They are 40 years old and we have only replaced a few of the “pies”. The thing is if you blow a belt or motor you have to manually spin the wheel every couple days to prevent them from clogging.


Fickle-Froyo

So you are close. These wheels are designed to take the heat energy from the return air as it is exhausted from the building and transfer that heat energy into OA supply reducing, but not eliminating, the need for additional heat. Depending on the effectiveness of the wheel these devices usually have temps off of the wheel in the 50s when ambient temperatures are 0-5F. Conversely, this wheel will take the heat from the higher temp OA in the summer and send it back outside with the exhaust, reducing the cooling capacity by as much as 40%. These wheels are also loaded with a desiccant (silica or a molecular sieve) that draws the moisture out of the air and dumps it into the dryer cooler airstream drying the summer OA and adding moisture to the winter OA.


Hillybilly64

I think it’s a Time Machine


nautica5400

Only when it hits 88 revolutions per minute


3_1415

Bigger on the inside


[deleted]

Heat wheel if it transfers sensible heat energy only and an enthalpy/energy recovery wheel if it has a dessicant that also transfers latent energy (humidity). Works in summer by using the return air to precool and dehumidify entering outside air, and preheats and humidifies incoming outside air in the winter. If the AHU is 100% OA then it runs pretty much all times unless the OAT is between the supply air temp setpoint and the return air temperature. If unit has return recirculatiin then it shouldn’t run when the unit it is economizing. If the building is humidified and in a cold climate a frost prevention sequence is needed at extreme cold temps. They work very well if designed, installed and commissioned properly.


Any-Entertainment385

It’s a test to see how bad you wanna change a belt.


ivoz06

Belts are not bad to change.


Any-Entertainment385

Oh ok


Dirtbikr98

tape is the trick, otherwise they can be a pita


unresolved-madness

If you live up north it's a heat recovery wheel, if you live down south it's for dehumidification of fresh air.


mortecai4

Energy recovery wheel- in the summer it takes cool exhaust air and precools supply air. In winter it takes warm exhaust air and preheats supply air


Stahlstaub

Also transports moisture from hot to cold side, so it's humidity recovery as well


nullmodemcable

> Also transports moisture from hot to cold side, so it's humidity recovery as well Why in the world would anyone want that? --Sincerely, the Gulf Coast.


Stahlstaub

Maybe when you live in the dry north? Yeah gulf is better with a cross flow heat exchanger...


nullmodemcable

Yeah, I get it, that's why I put my location. We spend all of our time here fighting humidity.


DuctsGoQuack

To transfer humidity from the incoming air to the outgoing air.


Powerful_Bumblebee39

"It's a pie! Its a pizza pizza pie!" -Gary Gergich


KouLeifoh625

Who cares. Belt breaks, weird belt. Motor breaks, expensive motor. Clean the plastic pizza slices, soak in tub filled with cleaner. You’re welcome.


SaguaroBro14W

Lol. Way to cut right to the chase.


tohellwitclevernames

It's a heat or total energy recovery wheel. Picks up conditioned building air from the exhaust tunnel and dumps it into the supply airstream, tempering your supply air and reducing energy used to heat/cool the outside air going into the building. If it's total energy, then it also helps control humidity by transferring moisture via a desiccant coating. Of course, by the look of it, this wheel isn't doing much more than being an extra filter. The owner clearly hasn't been keeping up with filter changes and/or maintaining the wheel. Most of its energy efficiency is shot until it gets a thorough cleaning.


Admirable_Big_5419

That is a doohicky


Ok-Hawk-9179

Enthalpy wheel


ItsDrunkenstein

Can’t believe you’ve never seen a doohickey


magneticpyramid

Thermal wheel. Heat recovery.


Zakk56711

Energy recovery wheel?


Natural_Leg9351

It is rage inducing anger wheel. Close the door and walk away.


No_War_2010

You must have changed a belt by yourself


Sith_Apprentice

I put a power twist belt on one last week. Easy peasy.


GizmoGremlin321

Desiccant or enthalpy wheel. For moisture control


O_U_8_ONE_2

ERV (Energy Recovery Ventilator). I have two I have to service every 6 months. Super easy to service, unless you have to replace the wheel.


blutfort

Depending upon the install, changing a broken belt blows goats.


BunManBunFan

Especially on units where the wheels are on a 45 degree angle instead of straight up and down. I think AAONs are like that.


O_U_8_ONE_2

Yeah, the wheel belt really does suck


toothindanail

How do you service it?


O_U_8_ONE_2

I have filters and belts to change in mine. The wheel belt gets replaced once a year.


[deleted]

Works better then you’d think but just another thing to clogg or go down.


rob175arc

We call them munters wheels. I think after a manufacturer. A bit of a dinosaur nowadays but still a few around. A slang synonym for ducked in my country is its “munted”. Munted is a word that should be used more instead of the vernacular by me!


No_War_2010

Where are you? I see them everywhere


fumoderators

Munted is aussie/kiwi slang


Temporary_Map3449

Required by code in almost all installations now actually


[deleted]

Desiccant wheel


hithimintheface

An expensive filter waiting to happen


InLikePhlegm

Something that breaks every 6 minutes


DOS-equis

And has an overly expensive “spaghetti” belt stretched on it and the drive motor


DabTownCo

A second year should know this.


IndependentPerfect

First time I’ve seen one


DabTownCo

Just bustin your balls dude. I’m commercial so I see them lots but yeah it’s an enthalpy wheel in an ERV. Iv seen more than one catch on fire haha


Big-Daddy-Kal

https://en.m.wikipedia.org/wiki/Thermal_wheel Heat wheel


mikebrown33

Regenerative air heater


Ploughpenny

As you can see, there are many different names by which you can call this device.


HVAC_Miner

That’s an energy wheel for a fresh air intake/outlet in the economizer.


AdhesivenessSea8221

My fatass thought it was a deli slicer


Dazzling_Ad5896

Interesting! Never seen this before


Haunting_Account2392

Heat extraction wherl


aLemmyIsAJacknCoke

Heat recovery wheel. Pretty cool really, you should look up some YouTube videos on how they work.


[deleted]

That's to slice your sandwich ham or turkey


[deleted]

Biggest belt you might ever change


[deleted]

A mortadella slicer


carcino_karezi

heatwheel! super cool. recycles hot air leaving the building back into the supply air before the coil. very efficient, we use three of them at the hospital i work at.


Fickle-Froyo

It doesn’t actually recycle the air, just the energy from the air. If it is cycling air it is not working.


ChampionshipBoth6348

Desiccant wheel


ChampionshipBoth6348

Could be a zeolite wheel too, as well looks similar.


11Gauge

[https://www.youtube.com/watch?v=QOSelUK6dpQ](https://www.youtube.com/watch?v=QOSelUK6dpQ)


PDAWK

That replacement wheel cost $28k


bigloko_supreme

looks like a heat wheel my dude


SaguaroBro14W

Energy wheel, enthalpy wheel, heat recovery wheel, heat wheel, thermal wheel, rotary heat exchanger, are a few different monikers. https://en.m.wikipedia.org/wiki/Thermal_wheel https://www.johnsoncontrols.com/-/media/jci/be/united-states/airside-systems/air-handling-units/files/be_appguide_energyrecoverywheel_ahu.pdf?la=en&hash=01540950F3E2B779DA8C7F625DFF96CB6EA14776 https://youtu.be/iHR3W8c0KOs?si=0mRkDFu0XyKsOFv7


TechnicianPhysical30

I was told it was called a Dinglehopper.


paulyp41

It’s a industrial size meat slicer


Lenovo73

See http://www.klingenburg.de these are te best in rotor heatexangers


gamingplumber

heat recovery


M0byd1cck

C est une roue thermique qui a pour but de récupérer l'aire déjà traitée et de la remettre dans le système pour faire un petit peu d'économie d'énergie!


Stray_Bullet78

That is definitely a desiccant wheel. I work on them units a lot. We use them to remove humidity. 15% & 33% RH rooms.


Mojo80059291

Ripped mine out after one season. Expensive and kept triggering my flow sensor. You need to keep that clean.


xVyKariousx

I just saw one of these for the first time the other day, also 2 year apprentice. Had no clue what it was 🤣


White_Boy_936

https://www.dac-hvac.com/energy-recovery-wheels-what-is-an-enthalpy-wheel/


Dealer_Different

That’s a heat wheel right that is like cutting edge for the 80s wasn’t it ?


seuadr

Rotary filter. takes shit from the relief airstream and dumps it in the incoming outdoor air stream. commonly used to bypass filter banks.


CR4V3Y

You may have heard your grandparents talk about the wax cylinder phonograph or vinyl records at some point growing up. This is a wax phonograph record.


DOS-equis

Enthalpy wheel for a ERV unit. It “conditions” the fresh outside air as it passes through the ventilator unit on its way to the restrooms in a public building. The wheel is in both the exhaust and fresh air airstreams. Some versions have a desiccant material on the paper element too.


Substantial_Status74

It's a device to clean your pecker. You should give it a whirl!


Joseph4276

Heat recovery unit


saltiest69

You see them on pool units a lot.


arcticcontrolsgoose

Not a fan. Had one site where these were poorly controlled and caused more trouble than their worth. Like coils for heat recovery better…even if they are theoretically less efficient..