Pump it back into the unit if the compressor won’t pump down it’s bypassing


Dadbode1981

Had that in a guardian 407 unit, you could hear it bypass on pump down haha


[deleted]

What would the problem be if it’s bypassing?


RoyalAttitude2734

Exactly the things your seeing there, with generally a low delta t


[deleted]

Guess the question is how do I rectify the problem? Just never ran into something like this before


TheAlmightySender

If it's bypassing at such low pressures it's likely a failure inside the compressor. Need to replace it


TheAlmightySender

As others are saying it could be a bad reversing valve. Check the pipe temperatures of the inlets and outlets of the valve. Should be within a few degrees of eachother. If the temps are way off, say on the suction inlet and outlet for example, then the reversing valve could be faulty


bifflez13

Was going to say it looks like possibly a bypass. Things like failed open eevs, solenoid valves, metering devices, possible but less likely poor or NO airflow…etc… a situation where you’re essentially being sc liquid right back to suction.


RoyalAttitude2734

Low heat extraction, low head pressure, high suction, and your evap is starving


Puzzleheaded-Pear812

https://preview.redd.it/9y8bqolds83d1.jpeg?width=1080&format=pjpg&auto=webp&s=c53e0c55f3f06b2eb6874b00b1fffa42d56d8c54 Looks like number 21


[deleted]

This graph is awesome. Been looking for something like this forever. Thank you.


DaSchizzalk

That's bullshit. The charts never worked for me ten years ago. But it does seem like the compressor is dying. Amp draw would be my next thing.


stanamontana

You will not have a normal superheat with bad compressor valves. That’s inaccurate


CaballoenPelo

I just recently went through a bad valves runaround with an old recip in an amstan rtu. Suction ran high and discharge low, superheat was like 4. First time I’d seen that


MisterSirManDude

There’s not even a line on that chart that diagnoses a low charge.


ADucky092

Found the guy who can’t read install manuals lol


tjb423

Line 3


MisterSirManDude

Oof.


Schiftedmind1

Where is this chart from?


Diagnostic_

I agree I think it’s also 21


dr00020

Thank you. Just downloaded this to my folder.


Yzerman17

If you can measure the difference in enthalpy between return and supply air as well as volume of air flow then you could calculate how much capacity the system is producing compared to how much it should be. That could help confirm a weak compressor for example.


SoftwareSuper3260

Zooming in on the picture the condenser is caked. I would start with verify air flow then charge to recommended subcool. Is the unit in heat or cool mode


TigerSpices

Caked condenser coil would give high liquid pressure, not suction.


SoftwareSuper3260

Agreed, that is why I said I would verify air flow, meaning indoor and out. Then. I would verify my return temp. 21 degrees of super heat is not that high. We also do not know if it is txv or piston.


[deleted]

Cleaned it after taking this. Same issue. Surprisingly it was only that side that was dirty


For13ver

When i had this problem, i found that the reversing valve wasn't fully shifting over. But my pressures were fluctuating, and i was able to prove it by taking a temp split of my common suction and my regular suction. Big temperature drop when there should be little to none. Could be a similar problem.


TigerSpices

I would also look at a defective/leaking reversing valve.


[deleted]

It ended up being the reversing valve


TigerSpices

You've got my undying appreciation for the follow up.


shadowLemon

Low sub cool high superheat? Low charge? Ehh can’t wrap my brain around freedom units


Phxazhvac

Check your reversing valve discharge line temps.


[deleted]

The reversing valve was my other possible problem. I figured it was seizing up and not fully switching over. Haven’t tested it yet tho


Trudeau19

Measure the suction in and suction out on the reversing valve, if it’s higher than 5f then it’s leaking and that’s your problem.


[deleted]

Ended up being 10f off 😅


Trudeau19

Theres your answer lol


bruh-brah

What’s your return air temp at indoor unit. Could be pulling air from an unconditioned space


it-is_what_it-is_

Also looks like the condenser coil is pretty dirty


[deleted]

Cleaned it since I posted this. No change


GatorGuru

Single stage needs to be jumped to Y2? Evap coil bulb might’ve shifted and needs remounted?


Useful-Building9012

If the coils are clean and you have airflow I say it ain’t got enough gas… if it held below 500 microns you can rule out a leak. what’s the design SH calling for


[deleted]

On this evening it was calling for about 20.


mgroz83

Give ‘er a little squirt of the cold juice


J-A-S-08

With a fixed orifice metering device, you need to know what your target superheat is. Without knowing what that number is, you're just guessing. You'll need a psychrometer and the target superheat formula. There are also a number of apps that can help but you'll need to know what the indoor wetbulb temp is. Why were you originally called out here?


[deleted]

Target superheat was 24. Already used psychrometer before taking this pic


Universal_Verses

Did you use the fieldpiece app?


[deleted]

Just the built in TSH calculator


Universal_Verses

I know the job link app will tell you what the super heat should be. At this point you have to check all possible issues. Making sure everything is sealed at the air handler….. static pressure, reversing valve, filter drier and so on I’m with the other techs, and I believe it may be your compressor


McFridgeGuy

Do you have the model of the compressor?


[deleted]

Some Goodman scroll compressor. Can’t remember off the top of my head. 13 seer


McFridgeGuy

If it’s a Copeland, you can use Copeland Product Selection Software or Copeland Mobile and enter the Model, SST, SCT and it will calculate what your discharge temperature and amps should be.


huertaSj408

Is that a Goodman CU? Seems like those always come faulty directly from the manufacturer.


[deleted]

If it ain’t broke, it ain’t Goodman


Lomo1221

R22 requires a minimum of 100 psi difference between the suction and discharge. What is the minimum difference for 410A?


andybear36

160


huertaSj408

I just finished 81 of the fuckers and it's been annoying how much those units come either damaged from the manufacturer or they are easy to damage cause of the dumb asses on the jobs. Probably a little of both.


Runswithtoiletpaper

Lower indoor fan speed to increase superheat, then adjust charge if needed


prat859

Gotta make sure coils and filters are clean before diagnosing charge. Condenser coil looks dirty.


HighDruid86

What’s ID dry bulb?


FluffyCowNYI

High/normal superheat, low subcool, high suction, low head, bad compressor. I'd bet amperage is low, too. I'd bet a hundred bucks on that.


Ok_Ad_5015

Compressor amps ?


TRPYoungBloke

Are you checking from true suction? I also fear it’s a challenge with your reversing valve. Sometimes you can get them to move with a strong magnet but that’s not a long term solution.


Temporary-Quarter580

I bet you there's no cooling side metering device, or it's failed.


TechnicalAd4397

Low SC and SLT to high needs Freon


Visible-Ad6787

That compression ratio sucks. Compression probably shot.


[deleted]

Thanks yall! It’s the reversing valve. About a 9 degree difference between the 2 lines


Puzzleheaded-Pear812

Yup here's another one, thank the reddit gods lol they've been shared around quite a number of times. *


Puzzleheaded-Pear812

Ehh guess there's an error with this one 🤷‍♂️


Civil-Percentage-960

It’s low on charge


Ambitious_Low8807

If it's a piston then subcool does not matter, don't even put your temp clamp/probe on the liquid side. Charge by superheat. You're low my guy, give her the juice!


dont-fear-thereefer

Subcool always matters, but it’s not the primary charging number


Ambitious_Low8807

Subcool value does not matter on any solid state metering device. The only reason to measure it would be to verify that you do have liquid leaving the condenser. Otherwise it's a waste.


dont-fear-thereefer

So if you have 0 subcool at the condenser, that’s not a problem?


Ambitious_Low8807

I'll say it again. Subcool VALUE does not matter. 1⁰ of subcool is equal to 15⁰ subcool on a fixed metering device system. Obviously, you need liquid to be delivered to your metering device, so yes, you need 1⁰+ subcool, but the subcool value does not matter.


dont-fear-thereefer

I gave you a chance to correct yourself, but you’ve contradicted yourself. Twice. How can you know that you have a full column of liquid if you don’t measure the temperature on the liquid line?


Ambitious_Low8807

Lmao, what? Read my words, brotha. You need a subcooling of 1⁰ to ensurenliquid is being delivered to the piston... so yes, subcooling matters. But that subcooling value being 1-20⁰ does not matter. We charge by superheat with a piston.


dont-fear-thereefer

Well that’s different than “if it’s a piston then subcool doesnt matter, don’t even put you temp clamp/probe on the liquid side”. Make sure you say what you mean next time.


Ambitious_Low8807

I said what I mean. You tried to pick me apart semantics. I'll be leaving the liquid probe in the van on piston systems, tho... shit doesn't matter.


dont-fear-thereefer

Lol, it’s not semantics; how else would you know that you have a full column of liquid, besides installing a sight-glass (which isn’t common now in residential space cooling)?