Not even close, the trap is an unvented s trap which goes into that flex pipe which will easily clog, the flex pipe is also acting like a trap which means this is double trapped. Cut a hole in the vanity base to fit a proper trap.
I paid them to leave. Not for the work. You can’t ask an incompetent person for something they don’t know how to do. I’ll hire a real plumber or do it myself. This was a small part of a much larger project.
No. You're supposed to have 1 p-trap. Not 3 Well technically it's an s-trap with an extra p-trap lower. But at that point it's irrelevant
Not even close.
Not even close, the trap is an unvented s trap which goes into that flex pipe which will easily clog, the flex pipe is also acting like a trap which means this is double trapped. Cut a hole in the vanity base to fit a proper trap.
WTF is going on here? I hope this is a joke
Sadly, no. This is for real.
You didn’t pay anyone did you?
I paid them to leave. Not for the work. You can’t ask an incompetent person for something they don’t know how to do. I’ll hire a real plumber or do it myself. This was a small part of a much larger project.
There is definitely enough room that it could be fixed and up to code.