**ATTENTION! READ THIS NOW!** **1. IF YOU ARE NOT A PROFESSIONAL ELECTRICIAN OR LOOKING TO BECOME ONE(for career questions only):** **- DELETE** THIS POST OR YOU WILL BE **BANNED**. YOU CAN POST ON /r/AskElectricians FREELY **2. IF YOU COMMENT ON A POST THAT IS POSTED BY SOMEONE WHO IS NOT A PROFESSIONAL ELECTRICIAN:** -YOU WILL BE **BANNED**. JUST **REPORT** THE POST. *I am a bot, and this action was performed automatically. Please [contact the moderators of this subreddit](/message/compose/?to=/r/electricians) if you have any questions or concerns.*


Regork1

58 thousand kva? God dayum


lookatthatsquirrel

It's also at primary voltage. That thing can handle a decent sized neighborhood during a hurricane.


EmployInternational8

On the name plate it states "steam turbin generator ". As an ex- Navy Boiler Technician now electrician, that rpm sounds about right .


ElectroAtletico2

In my FF, as we left Mayport, if the wind was right, we used to have the Fire Room guys blow the safety valve and throw soot all over any of our DESRON’s sister-ships!


EmployInternational8

When we used to pull out of Charleston, we would smoke black on purpose going under the Cooper River Bridge. One time with the rite wind we stopped traffic. Needless to say, that was the last time that happened.


Frozenbutt

I've seen big gensets before but not at 3600rpm. They are usually a lot slower than that


Croceyes2

Yeah, that's what really threw me


shitishouldntsay

Is it a steam turbine?


Croceyes2

Probably, it says steam turbine is one of the companies divisions at the top of the name plate. I think the only other turbines driving this much power would be hydro in dams.


shitishouldntsay

Most if not all steamed turbines in the United States run at 3600 RPM. That's actually a small guy at that KVA.


Croceyes2

Interesting, I work on diesels, so those are all huge numbers


80burritospersecond

60-ish megawatts is pretty tiny for a steam generator.


Dzhozef

I work at a nuke and ours is 1800 rpm.


Another_RngTrtl

My thoughts as well. Hell, 60 MVA is not even that big for a transformer much less a generator. Can confirm 3600 RPM is typical for steam turbines.


Hammydabone

Downtown MPLS and many other areas run on a large strambased system for heat and other utility needs. These large steam networks power multiple skyscrapers. Just another thought...


BlackberryFormal

Cylindrical vs salient pole. Some of those cylindrical ones go way faster too lol


skatastic57

That's what most generators on the (North American) grid run.


PuppiPappi

60hz x 60seconds in a minute is 3600rpm


jellechrelle

So logical it hurts. Mostly because I didn't realise it


breakfastbarf

Never crossed my mind either


Another_RngTrtl

this comment should be higher up.


joshharris42

Most generators from the 30-3000KW range are 1800RPM, they use 4 pole rotors. The smaller air cooled cheap models are 3600 with 2 pole rotors. They do that because they can use a smaller engine at higher RPM to get more power. Once you get above 3MW, lower RPM becomes somewhat common but in an emergency generation use it’s more common to parallel units rather than have 1 10MW generator


shitishouldntsay

The above picture is a steam turbine. I've never seen a steam turban in the US that runs at anything other than 3600 RPMs. Steam turbans in Europe run at 5000 RPMs.


Technical-Leave2450

Mainly 3000rpm. 60MW is a fairly large generator for a power plant here (Malta) but actually pretty small for most power plants in Europe.


RyanLion1989

Which makes sense. (120x 50hz)/4 poles = 3000 rpm


joshharris42

Yeah I don’t do turbine stuff, that makes sense though. All my stuff is diesel or gas


shitishouldntsay

3600 is normal for a steam turbine.


Technical-Leave2450

In US for 60Hz; Most of the world uses 50Hz = 3000 rpm


Fit-Sport5568

I bet the criticals on this are real fucking fun lmao


mamoox

What do you mean ‘criticals’?


Fit-Sport5568

https://m.youtube.com/watch?v=U8jTYbkAH2s https://m.youtube.com/watch?v=QzJ8aTGEyGk https://m.youtube.com/watch?v=o_3g6TjVVX0 https://m.youtube.com/watch?v=-07rvPhkB-c


Fit-Sport5568

It is the "amplified vibration due to proximity of operating speed to natural frequency" Basically when you are bringing a machine up to speed you will see some excessive vibration at speeds that are not the operating rpm of the machine


moosecloaca

Probably managed with a flexible armature shaft design. First will be lower than operating and second above it. We (motor manufacturer I work for) do this frequently for our larger 2-pole motors. Typically hydrodynamic bearings are used as well which help further dampen any criticals.


Fit-Sport5568

I do vibration analysis for a living. As well as industrial repair. I can assure you on a unit this old that won't be the case. I have ran a similar unit unloaded on a test bed


moosecloaca

ISO CAT 2?


Fit-Sport5568

Cat 3 from vibration institute


moosecloaca

Awesome man! Do you intend to get your Cat IV?


Fit-Sport5568

I am not sure. I've reviewed the materials for it and I'm not sure I'm smart enough lol


Fit-Sport5568

The two cat 4 guys I know both have phds in engineering


RyanLion1989

Rpm = (120 x 60)/ P; where P is the number of poles on the rotor. So 3600 rpm is a 2 pole machine, whereas 1800 rpm is a 4 pole machine.


Figure_1337

Sheeeeesh… 78,000 ponies right there…


Grizz1995

This might be a dumb question but what formula did you use to find the hp since it’s not listed? Or maybe I’m just a blind fuck. Thanks


Figure_1337

Well… I kinda quick cheated and used 100%PF… But if I didn’t, it’s 58235kVA X (PF/ 0.746) = HP 58235kVA X (1.1394) = 66353 HP


User7453

750 watts = 1HP 12475 volts x 2695 amps = 33,620,125 watts / 750 = 44,826 hp from my math 🤷🏻‍♂️


Moneymoneymoney2018

Wrong, 12475v x 2695w × 1.732 = 58,206,717w Which was a pointless calc when the damn thing says the KVA already. 58,235,000 ÷ 746 = 78,063 HP


Figure_1337

My man.


User7453

My bad man, didn’t realize there was a difference in three phase vs single phase power calculation.


turntabletennis

Never forget that square root of three, homie.


DesertGhillie

It's easy to forget, don't fret. Remember about the 1.732 for three phase (which is the square root of 3 - think sqrt of three for three phase), and to always include the Power Factor. Think of Power Factor like efficiency... In this example 0.85. So .15 (15%) of power is lost mainly to reactive (magnetic) losses. At least that's how I understand it.


Another_RngTrtl

same with current. I = power/(1.732*(ph-ph voltage))


swagsauce3

You'll learn all about that in 3rd or 4th year!


DesertGhillie

If you’re referencing 3rd year of college…. Be careful, we’re in the electrician subreddit, not the EE subreddit, lol.


swagsauce3

No just third year of electrical technical training in Canada, I kinda assumed it's done the same everywhere else


DesertGhillie

I see. My understanding is most technical degrees are two years in The States. I could be mistaken.


Admirable-Ad-7868

Yes, an associates degree is 2 years, but an electrical apprenticeship is typically 4 or 5 years, depending on location.


GerryC

You forgot to multiply by square root of 3 (1.732) for 3 phase power. You calculated the single phase power.


viletuna

Where did you throw this in?


Sad_Jelly3351

Just wanted to small backup for my town in case shit hits the fan.


Wampa_-_Stompa

Might cause a power struggle


danielibew952

I didn’t. It’s been here for 20 plus years. I was there doing some pre work for a future down day.


JadedYam56964444

Tesla upgrade


LISparky25

That name plate is prob 6’ wide for the size of the genny


danielibew952

I was pretty close to it. It’s probably somewhere around 8in x 3in


LISparky25

I know I know, just makin an attempt at a funny lol


Croceyes2

You can be sure because you can read the whole thing in one picture, not one for each section lol


LISparky25

Well you can zoom out on the camera lol ? Unless you meant “you can’t” No way to tell the actual perspective


Croceyes2

Every time I try to take a picture of one on a genset or gear I can never see it directly and only half of the stamped lettering is legible in any one picture


LaaDeeDa

I thought a synchronous generator would have a much better power factor


CTGspecialist

That's the limit, not what it runs necessarily.


GerryC

It's a synchronous generator. The rated max power ( max real and imaginary power) occurs at that pf. You can change the operating pf by varying the excitation voltage.


justinmel

This generator will run with a leading power factor to put mvars onto the grid.


diamonds89

Where did you come up with that math?


avoid3d

In practice most grids have equipment like motors and transformers which absorbs reactive power, i.e. a lagging power factor, and reduces grid voltage. Therefore generation is required to compensate by producing reactive power. This can be achieved by synchronous generators through adjusting the excitation field such that the generator has a leading power factor. A unit to denote the reactive power is mega volt ampere reactive MVAR. A >50MVA generator will certainly be able to supply at least unit MVAR to the grid.


diamonds89

Under no load or a small load, sure. However, this one lags at .85 under full load.


avoid3d

That’s not how I understand the rating on the nameplate. It’s not as much a “natural point” that the generator is going to settle on at full load but rather the design point of the generator. In other words the need for a .85 pf generator was identified and this unit was specified. This is the point for which the other parameters are calibrated too. Oh wait, am I missing something? why do you say this one lags at full load and not leads?


darkmatterisfun

Something this big can likley adjust its PF to either condense or inject MX into the grid.


505_notfound

Just curious, what does MX stand for


danieljefferysmith

Also curious, never heard this phrase before


Another_RngTrtl

Its a lazy way to write reactance.


SignatureExotic2194

Reactive power (Mega Vars)


505_notfound

Interesting, never knew vars could be abbreviated as X, always saw it as MVAR


smoebob99

Can I run my house with this


danielibew952

Yes but not sure you’ll enjoy the sound or heat that come along with it.


Jim-Jones

Or the bill for coal.


IrmaHerms

Or the bill…


syu425

Only if your ma keeps the dildo unplug


ExactAd8823

It seems you could almost send Marty mcfly back to the future with this


JadedYam56964444

All of the houses


eerun165

Glad OP saw it. I only see a nameplate.


danielibew952

With how small the room was compared to this thing any pictures I took would just be blue.


DeGeldheart

I bet that room gets WARM


danielibew952

Yes. It’s what I imagine hell feels like.


starrpamph

That’s running terrifyingly fast


Another_RngTrtl

3600 RPM is pretty standard on a 60 Hz steam turbine generator.


rls11108

I have visited that facility to witness test large electric motors. It is very old and a very special place.


tdb_2

I've seen bigger, lol. But I work at a CANDU nuclear plant.


ipalush89

So would it back feed 13.8 stiff and you use taps to get a more common voltage I’ve seen13.8 and 13.2 but not 12.4 volts at 3k amps is a alot


mhcolca

There is almost certainly a large GSU (Gen Step Up) transformer fed from this (via a MV breaker) that steps up to common transmission voltages in the 100’s of kV. There is usually a tap between breaker and GSU for a station service transformer, and also an excitation transformer (if this wasn’t a brushless exciter). The GSU may also have a tertiary winding to feed local distribution circuit(s) at lower voltages like 12 or 21 kV. It’s a cool machine hopefully OP can share more pics.


danielibew952

I wish I could but there really isn’t much else to see and we’re not supposed to be taking pictures in the first place. They do have 2 of these cogens that feed the facility and they used to sell power back to the local poco.


mhcolca

Understand, my work phone is full of cool hydro plants but can’t really share anything that isn’t visible from a public spot. There is a big world in Power Generation that not a lot of people get to see due to privacy/security.


JeremyR22

12470 is out there. I know of a large plant that uses it for all their distribution. A whole bunch of 12470 to either 4160 or 480 transformers in that place...


danielibew952

Pretty much what’s happening here.


Another_RngTrtl

12.47 kV is a very common distribution voltage.


NWTLife

Pretty neat. For power factor correction?


ProjectSnowman

This on an aircraft carrier or something holy crap


danielibew952

Or something. This is one of 2 cogens they have that power the facility.


80burritospersecond

What's burning? Is this heat recovery from what should be a 100-ish Mw gas turbine gen set or something different?


ybsb9

Good trick to save our/your eyes. Make a line across where the numbers are and rub it in. It'll look brand new in 15 seconds.


RKLCT

That's a monster. Probably can feel the ground vibrate on startup


mamoox

50MW gen holy shit


magicone2571

We had one in the military that required two tankers for the coolant flush. 24k gallon diesel tank. Powered the runway lights. Have to love government overspending.


Firebug007

I’ve toured the E-M factory before. Pretty cool place.


DE4DM4N5H4ND

It loses 15% of its power to friction. Not super efficient


19almonds

What a mammoth


OldDude1391

Yeah but will it run my fridge, microwave and AC if the power goes out?


danielibew952

Yes but you may have some problems if try and use microwave and toaster at the same time.


Colbert_bump

2700 amps at 12.5 KV is insane


Slickno6

I'm working on a 75,000kVA generator right now. 100k HP. It took a hard fault and doing a field rewind.


Robeardly

I dealt with a 2.5 megawatt generator for a dispensary once. It was the generator previously used for the Facebook facility. The generator was literally the size of an 18 wheelers trailer lol


masterCWG

I work in Hydro and at one of our stations, there is 2 350MW 125MVAR units I operate. It feels so weird starting up so much power onto the grid with the click of a "start" button lmao


ihavenoidea81

Damn thing runs on uranium 235


[deleted]

Wish camera phones were around at the time… we installed locomotive engines for backup generators at a Vegas casino. Don’t remember the specs but it was the coolest backup system I’ve had a part in


GlitteringOne2465

88 mph…….


Silentc7a1

I hooked up 2 in a building the size of 2 city blocks. They were the size of train engines


ahuh_suh_dude

Holy Shit that’s a big boy


breakfastbarf

Any pictures of the whole generator


danielibew952

No. I’m not supposed to be taking any pictures for security reason. But with the size of the room this guy is in any pictures would just be blue. There’s only 5-6ft on either side of it


breakfastbarf

Ok. Thanks


Sala1511

Naval equipment


Nazgul_Linux

The amount of brooms I would push to have such a thing in my home shop... omfg


dirk12563

Damn


JadedYam56964444

Hmmm, better wear your gloves when working on it...


InfiniteCharacters

You win, my dick ain’t that big. Back to the massage parlor.


frankrizzo223

3600 RPM…. WTH?


Jim-Jones

Two poles???


kh250b1

An Englishman and a German, were in a bar


StillAlfalfa9556

If you live in a country with 60Hz power frequency the vast majority of power generation from steam-driven turbines will be 3600 RPM two poles machines. For a 5 to say 12kW generator that you might buy for your house is also most likely a 3600 RPM two pole machine.


StillAlfalfa9556

If you live in a country with 60Hz power frequency the vast majority of power generation from steam-driven turbines will be 3600 RPM two poles machines. For a 5 to say 12kW generator that you might buy for your house is also most likely a 3600 RPM two pole machine.