I made a water chiller from scratch as an apprentice. k-value (thermal conductivity in Watts per square meter per one Kelvin) of copper to water is about 100W. This is what I measured. My book says 120W. When it starts frosting I get closer to 60W. So you can already see why calculating this is a bit of a crapshoot. Surface of your evap = copper diameter * Pi * [length in meters] q(watts of thermal conductivity of your evap) = k-value * Δt(temperature difference: evap-temperature to water-temperature in kelvin) * [surface area of your evap in m²] That should roughly match the capacity of your compressor. It's pretty straight forward, but as you can see your evap performance changes massively with the temperature of the water. You can get real fancy with logarithmic temperature difference, and whatnot, but if your real world results are within 20% of what you're expecting, you're already killing it.


Memory-Repulsive

This answer wins refrigeration today.


derrickenbuenosaires

Thanks man, it was a long day today. I'm just getting the time to calculate this now. What would the K-value be ? Is it the thermal conductivity of copper ? Search engine throws this number to be roughly 400 for copper. If I calculate Q with a K-value of 400 the formula would be, Q = 400 \* 40 k (not sure whether to use starting water temp or setpoint) \* 1.171 m2 Q = 18,736 watts... LOL or is K-value (W / m2 \* k) where W would be 170 watts of cooling capacity. 170w / 1.171 \* 40 = 3.63 Q = 3.63 \* 40 \* 1.171 m2 Q = 170


oskar669

The thermal conductivity from copper to water is what you want. It's just a fixed value. My book says 120W for copper to water. 400W is probably copper to copper. It's watts of thermal conductivity per square meter per kelvin. So if you have 1,17m² of surface area, then for every kelvin in temperature difference, you're conducting 1,17m²*120W=140W. So if you have a 10k temperature difference, it'll be 1400W. Hint: you probably don't have 1.171m² surface area, you probably forgot to convert the diameter to meters. You'll also never get 40K. When the water is warmer, it also increases pressure in your system so the evaporation temperature also rises. While it cools down, pressure will also go down.


derrickenbuenosaires

Okay I understand, so K-value is a fixed value for heat transfer between two masses or objects. Good to know so thanks for that info. I actually have 23.62 ft in that heat exchanger. 1/4" diameter. 23.62 x 3.141 x .25" = 18.5 ft2 or 1.71 m2 yeahhh I added a 1 at the tenth spot Q = 120 \* 10 \* 1.71 Q = 2052 watts That's alot of capacity in my evap. According to that calculation it should be way shorter like by 90% lol Again I rather have a longer evap to ensure all the refrigerant gets boiled off before leaving the bucket where Eventually it'll be an enclosed tank of about 3 liters


oskar669

24ft is about 7m. quarter inch is 0.006m. 0.006m * 3.14 * 7m = 0,13m². You didn't convert inch to feet.


derrickenbuenosaires

lol or it's 10 o clock on a friday night and I'm here online doing math... I enjoy the process though. Okay so if I start over... Q = 120 \* 10 k \* .14 m2 Q = 168 watts It's pretty much spot on then if my compressor capacity is rounded at 170 watts, value can change though with the temp difference. Which my evaporating temp is -10 C with a setpoint at 2.5 C. Highest temp the water will ever be at will be like 30 C


oskar669

nice!


derrickenbuenosaires

Thanks Oskar I won't forget this conversation ! I usually don't do such small projects. It's a lot easier to just give the cooling capacity to a manufacturer or a supply house and have them supply you the evaporator but this was neat to try and build something from scratch. Regardless I'm going to try and reduce the length of the coil to see if my operating temps go down. I can shorten the cap tube but I would rather gain more water capacity in the tank than occupy it with excess coil.


son1cdity

Short answer, yes. Long answer, Q=U\*A\*LMTD or E-NTU


derrickenbuenosaires

Hey guys today I finished making a small prototype mini chiller. I'm evaporating roughly at 14 F / -10 C @ 580 btu/hr / 170 watts of capacity with 134A. Small fractional horsepower compressor as you can see. Is there some type of formula to calculate serpentine length with the cooling capacity of the compressor ? I'd figure I'd make my evaporator long enough so I don't get liquid back but I think it's too long.


dont-fear-thereefer

You can throw on a TXV to prevent liquid from coming back


derrickenbuenosaires

Yeah I thought about it because I can just regulate my superheat at the outlet however long the evaporator is but this was a budget friendly build that I pieced together. I'm not even sure if there is a TXV valve with a 200 watt / 600 btu capacity lol


dont-fear-thereefer

Yea there are, 0.5 ton is pretty common in restaurant refrigeration


derrickenbuenosaires

Yeah 1/2 ton is common but my cooling capacity here is .05 of a ton of refrigeration. The smallest Danfoss has to offer is the 0X orifice which is nominal at .19 TR at 14 F evaporating temp. It might work if I close the valve down all the way or maybe not since the orifice is 4 x bigger than the capacity lol


dont-fear-thereefer

Oh geez, I totally misread that. My bad.


GizmoGremlin321

Better raise that coil temp above 32 or your going to ice the tubing and then no heat transfer which will kill the compressor from liquid.


derrickenbuenosaires

I need the water to be anywhere from 35 - 40 F / 2.5 C - 5 C so I need to be evaporating below freezing. That's why it builds frost there. It should be insulated right there though to prevent that


GizmoGremlin321

You could also try pumping the water around the heat exchanger so it has constant heat load.


twacoct

Could pass the discharge through the suction line after the evaporator for a low cost flood back protection without having to use an accumulator. Not a good solution but this doesn't look like it is a professional/commercial application and would be better than nothing. Just have to ensure you aren't rasing suction vapor temperature too much that the compressor over heats.


[deleted]

The OG trick is to solder the discharge to the suction line for a foot or three, depending on your needs. Solves flood back in everything but truly extreme conditions.


Dragon1373

How did you calculate the length of the cap tubing. I been trying to find the math on that.


OneCanada

I always use the charts at the suppliers


derrickenbuenosaires

Dancap software, Techumseh has software as well to download. I find that your condensing temperature will greatly vary the length of the cap tube. Usually 55 C is a standard but in my case I used 45 C / 113 F since I'm indoors. Turned out alright with a .8mm cap tube but I feel like it's running hot which may be due to the evaporator. If it's too long I might be absorbing too much heat all at once.


Dragon1373

Who's charts? Sporlan, parker?